That thread shows more confusion.
Do posts on here ever get reported back to the relevant Committees? Geoff?
Why dont we get some guidance, as, at the moment, a boiler on a 1mm T+E circuit needs to be replaced in a rented house, as it does not comply, which is mad, as it is totally safe.
In fact 1.5 mm² T&E is no use for a power circuit because the CPC is only 1.0 mm² (524.1) unless it is a spur using an FCU (Appendix 15)
524.1 references Table 52.3.
App. 15 is informative, and doesnt show 10 or 16 Amp circuit protection, so obviously smaller cable is not used in the diagrams.
With good design, and circuit calculations, a 1mm conductor will be more than adequate for a 3 amp 'power circuit' load.
But it cannot be used due to Table 52.3.
https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=61562
That thread shows more confusion.
Do posts on here ever get reported back to the relevant Committees? Geoff?
Why dont we get some guidance, as, at the moment, a boiler on a 1mm T+E circuit needs to be replaced in a rented house, as it does not comply, which is mad, as it is totally safe.
In fact 1.5 mm² T&E is no use for a power circuit because the CPC is only 1.0 mm² (524.1) unless it is a spur using an FCU (Appendix 15)
524.1 references Table 52.3.
App. 15 is informative, and doesnt show 10 or 16 Amp circuit protection, so obviously smaller cable is not used in the diagrams.
With good design, and circuit calculations, a 1mm conductor will be more than adequate for a 3 amp 'power circuit' load.
But it cannot be used due to Table 52.3.