For large industrial plant, How to decide the number of panel boards for the lighting and small power services?
Is my below approach correct?

1. Breakdown the plant area/Electrical Room as per the layout.

2. Make the lighting calculation / socket requirements for the particular plant area / room.

3. Determine the number of fixtures/sockets to be connected in one circuit.

4. Determine the number of ways for each panel board considering the number of circuits (limit the voltage drop & balance the loads).
Parents
  • Former Community Member
    0 Former Community Member
    If it's just the lighting and small power, you could estimate that at say 40w/m2


    If you took an area of say 1200m2, that would give you circa 48kW, which is around 63A/phase.


    Put the board in the approximate centre of the 1200m2 area and that give you a circuit run out length of roughly 35m - which should happily handle voltage drop and impedance limits on "conventional" circuit sizes.


    Obviously, it's not that simple in a real site, as you'll be looking to put final DB's in specific allocated locations (E,C&I rooms, on plant galleries, out of harms way, reasonable close to feeder distribution or MCC run outs, etc)


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    If it's just the lighting and small power, you could estimate that at say 40w/m2


    If you took an area of say 1200m2, that would give you circa 48kW, which is around 63A/phase.


    Put the board in the approximate centre of the 1200m2 area and that give you a circuit run out length of roughly 35m - which should happily handle voltage drop and impedance limits on "conventional" circuit sizes.


    Obviously, it's not that simple in a real site, as you'll be looking to put final DB's in specific allocated locations (E,C&I rooms, on plant galleries, out of harms way, reasonable close to feeder distribution or MCC run outs, etc)


    Regards


    OMS