Visibility of BS951 Bonding Clamp

We have a problem with an over zealous pipe lagger.  Should the cable terminations or the whole clamp be visible on a pipe bonding clamp?
Parents
  • Accessible does not mean unlagged - so long as if you ever  need to inspect the connection the local lagging can be removed.
Reply
  • Accessible does not mean unlagged - so long as if you ever  need to inspect the connection the local lagging can be removed.