perspicacious:
....we recommend a 60% diversity factor is applied to the MCB nominal rated current where it is
intended to load the MCB' s continuously (in excess of 1 hour).
...
Hmm, so a EICR carried out on my dwelling with a 16 A circuit-breaker on my 3 kW immersion heater in a 210 litre cylinder would result in what code? ...
Well reading the rest of the advice, it only applies to close packed breakers, so no code if the breakers on either side were lightly loaded, or its suggests you should fit a 20A one if they are.
Perhaps they think we should fit 40A breakers to 32A rings to avoid stressing the breakers. I'd disagree.
I suggest that like the total demand diversity calculations themselves, where we see breakers totally 200-300A on a 100A company fuse with no issues , this is so much cobblers.
regards
Mike.
perspicacious:
Hmm, so a EICR carried out on my dwelling with a 16 A circuit-breaker on my 3 kW immersion heater in a 210 litre cylinder would result in what code? Assuming naturally that the rest of my dwelling electrics are perfect.................................
Just how big is your bath BOD?
Assume incoming water temperature is 10 deg C and you want 80 litres at 40 deg C.
It takes 1 calorie = 4.2 J to heat 1 cc of water by 1 deg C
4.2 x 30 = 126 J to heat 1 cc by 30 deg C
= 126 W for 1 sec
80 l = 80,000 cc so we need 126 x 80,000 W for 1 sec
a 3 kW immersion will take 126 x 80,000 ÷ 3,000 sec
= 126 x 80 ÷ 3 = 3360 sec or 56 minutes.
"The importance of education as well as technical understanding and also competent in the wiring".
Not such the assuming testing required but need the standard methods and using related testing to find the cause or problems.