davezawadi (David Stone):
There is a problem here. If the tenant does not want any work carried out (QUITE REASONABLY) then the landlord or contractor has no right to do so.
The Landlord has the option to bring legal proceedings, but is not obliged to do so - see R5 of the 2020 Regulations: Duty of private landlord to comply with a remedial notice. It would seem that, in effect, a tenant may veto remediation of an unsafe installation.
davezawadi (David Stone):
The law is badly drafted and does not explain how this requirement can be met with sitting tenants.
That's the nub of the problem. If it has to apply to sitting tenants it needs further legislation to allow a landlord to update wiring against the tenant's wishes.
It would be easy to amend the law such that a new EICR is only required for new tenants and only if the existing EICR is older than 5 years. Or maybe always have a new EICR for new tenants.
JPCoetzee:davezawadi (David Stone):
The law is badly drafted and does not explain how this requirement can be met with sitting tenants.That's the nub of the problem. If it has to apply to sitting tenants it needs further legislation to allow a landlord to update wiring against the tenant's wishes.
It would be easy to amend the law such that a new EICR is only required for new tenants and only if the existing EICR is older than 5 years. Or maybe always have a new EICR for new tenants.
Quite possibly a Landlord does have a right of access for essential maintenance, but that would require the sort of legal proceedings to which Reg 5 refers and about which I know nothing.
Sparkingchip:
However if anything goes wrong the question will be asked why you let the tenant move in when you knew it did not have a CPC.
Assuming the previous EICR recommended improvement why didn’t you act on the report will be the question.
Your reply that you still don’t consider it needs improvement may require dome explanation.
I DID act on the report. The previous EICR said there was no CPC in the lighting circuit, so I changed all light fittings to Class 2.
JPCoetzee:
I DID act on the report. The previous EICR said there was no CPC in the lighting circuit, so I changed all light fittings to Class 2.
If I were the Judge, I might well find that JPC acted reasonably and that further remediation was unnecessary; but I would have to consider carefully the expert reports of Peckham and Stone and prefer one or the other. Judges never sit on the fence - balance of probabilities is only 50. ... 1%.
However, as with engineers, there is plenty of wriggle room. One day you might win, another day you might lose. ?
I have to say that because of the additional protection, I favour C3. Yes action has been taken, but the circuit is still non-compliant, so it must be at least C3 until it is rewired.
I fear that further discussions of this nature will follow. ?