Alan Capon:goldenboy1818:
. . . The meter tails will only be about 800mm too long and not visible . . .Which is 27% longer than the maximum length the DNO specify.
If you did the same in my employers area, you would not get either the meter or the cutout fuse until you complied. We specify 2.500m maximum length to make it clear this is a maximum value. We would also walk away if a customers switch fuse appeared in a meter box. If there really isn’t anywhere else for it, you need to get the builder to sink a second meter box next to the one provided for the DNO’s exclusive use, and put your switch fuse in there.
Regards,
Alan.
Hi Alan, out of interest, would your company be happy to have un-inspectable tails enclosed in the building fabric as suggested by the OP?
OP, sounds like you need to ask the relevant DNO what their requirements are.
OlympusMons:
Hi Alan, out of interest, would your company be happy to have un-inspectable tails enclosed in the building fabric as suggested by the OP?
We are interested in being able to see everything up to and including the meter, then sufficient to determine the length and type of tails up to the customer’s first overcurrent protective device.
Regards,
Alan.
goldenboy1818:
Tails would be less than 3m , only thing switch fuse wouldn't be a suitable height
That's what I call being stuck between a rock and a hard place. ? Bear in mind that a switch fuse is a type of distribution board!
The old fashioned way was to have the service head and CU more or less adjacent to each other. Then came these external meter cabinets, which certainly avoided any difficulty with meter reading; but now even without a smart meter, it seems that meters are very seldom read.
I see two solutions: (1) install a switch fuse in an adjacent cabinet; (2) get the service head put indoors.
If tails are to be put in the wall, I repeat my question - how will they be supported?