Chris Pearson:goldenboy1818:
They have already fitted a isolator (not fused) and room in the white box is very tight nowDoesn't help!
The height of the CU isn't a hard and fast rule, but the idea is that an occupier in a wheelchair should be able to reach it.
I would be very careful on consumer unit heights
https://www.labc.co.uk/news/dont-forget-building-regulations-part-m-change
I also wouldn’t fit a switch fuse in the meter cabinet. Have you done the 1st fix? Could you possibly fit a flush consumer unit downstairs?
goldenboy1818:
. . . The meter tails will only be about 800mm too long and not visible . . .
Which is 27% longer than the maximum length the DNO specify.
If you did the same in my employers area, you would not get either the meter or the cutout fuse until you complied. We specify 2.500m maximum length to make it clear this is a maximum value. We would also walk away if a customers switch fuse appeared in a meter box. If there really isn’t anywhere else for it, you need to get the builder to sink a second meter box next to the one provided for the DNO’s exclusive use, and put your switch fuse in there.