Hello, 
I have the following problem with the preliminary design stage of a residential area:

The software I use can calculate a theoretically optimal location of a distribution substation for low-voltage networks. This place is calculated as a "center of power demand" or "center of gravity" of electrical consumers.

If the substation locates in this optimal place, we can design 0.4kV distribution feeders with a minimum length and power losses in low-voltage feeders are minimal. 

I understand it’s almost impossible to put it exactly there, and I consider some sites nearby. But the architect believes that this is unacceptable in terms of landscape design and wants to place the substation in a far corner.

Who should be the arbiter in this situation?  DNO representative takes a neutral position.  Local authorities are completely on architect side, they do not care that long power cables will heat the atmosphere for many years to come.

3602925e57eac86d03447a5e59fc8e9b-huge-image.png
Parents
  • Former Community Member
    0 Former Community Member
    Alex Juhanson:
    These are individual residential buildings of 2-3 floors. Heating is gas. Cables will be selected and designed in the next stages. With a high degree of probability underground Al 4x240mm2 will be used.


     


    Are you sure ? - given you only have circa 9 properties per phase, and gas heated buildings, I would have thought the feeders would be much smaller than 240mm2  - even in aluminium.


    Assuming for such a small number of houses, you aren't planning any backfeeds from other systems or between systems, then typically feeders would be 185mm2 with service cables being 25mm2 (single phase)


    185mm2 is usually selected over 95mm2, as it provides for future flexibility - if you really need more than a 185mm2, then the next "optimum" size would be 300mm2


    Regards


    OMS


Reply
  • Former Community Member
    0 Former Community Member
    Alex Juhanson:
    These are individual residential buildings of 2-3 floors. Heating is gas. Cables will be selected and designed in the next stages. With a high degree of probability underground Al 4x240mm2 will be used.


     


    Are you sure ? - given you only have circa 9 properties per phase, and gas heated buildings, I would have thought the feeders would be much smaller than 240mm2  - even in aluminium.


    Assuming for such a small number of houses, you aren't planning any backfeeds from other systems or between systems, then typically feeders would be 185mm2 with service cables being 25mm2 (single phase)


    185mm2 is usually selected over 95mm2, as it provides for future flexibility - if you really need more than a 185mm2, then the next "optimum" size would be 300mm2


    Regards