UKPN:
Loss of neutral and EV chargers, WOW! this should be interesting. What do the wiring regulations say??
Regards, UKPN![]()
Well it depends what wiring regulations you are referring to. Here in the North of Ireland we are in a perennial state of confusion with half the population wanting to remain in the U.K. and the other half thinking that the future would be better in an all-island republic. For the moment I can have one foot on ground  to which BS7671 applies while the Irish Regs is applicable to the ground on which the other foot stands. Despite your little quip, UKPN, I think that you know full well that there are several expansive ways proffered in BS7671 with respect to EV charging which are designed to address the issue of a lost neutral in a PME installation. The Irish Regs (IS10101: 2020) on the other devote only 3/4 of a line; “In TN systems the final circuit supplying a connecting point shall be a TN-S system”. My understanding is that this regulation is not modified from HD 60364-722
Edit; maybe if GK reads this he could confirm or otherwise that last sentence.
lyledunn:
The Irish Regs (IS10101: 2020) on the other devote only 3/4 of a line; “In TN systems the final circuit supplying a connecting point shall be a TN-S system”. My understanding is that this regulation is not modified from HD 60364-722Edit; maybe if GK reads this he could confirm or otherwise that last sentence.
Confirmed, although the Clause number is 722.312.2.1, and the requirement is
In a TN system, the final circuit supplying a connecting point shall be a TN-S system.
Interestingly, in IEC/HD speak, this does not mean the supply arrangement has to be TN-S; there are many international standards, which have the notion that in a TN-C-S, downstream of the point of separation of the protective conductor is TN-S.
As an aside, this creates a unique situation in interpreting those standards which are not incorporated in BS 7671 in the UK. For example, does BS EN 60079-14 permit the electrical installation in a hazardous area to be derived from a TN-C-S (PME) system?
I would also add that, whilst the UK is presently the only country whose national wiring standard is concerned with the risks of broken neutrals in TN-C-S supply distribution arrangements, other countries are beginning to consider them, as we have seen with the recent discussion thread here.
... and finally, I understand for the rest of the UK, we are looking at a recorded average of just under 1 broken neutral event reported today, but the YoY rate of increase is perhaps more concerning. I have not seen specific data regarding damage to equipment or installations, injuries, or worse, just "events".
Wdavezawadi (David Stone):
Yes Mike, I am suggesting that a fine is necessary in order to prevent it happening often, figure from the HSE guy I was speaking too the other day was more than 1000 incidents last year. This is simply down to network maintenance being inadequate, a lot being from 1930s (where I live) and a lot more being older.
Would anything be gained by requiring the replacement of old infrastructure, unless there was also a requirement to return to "proper earthing" rather than PME.
Replacing an old DNO main with a new one will require at least two new joints per customer, one joint between the new main and a new section of service cable, and a second joint between the existing service cable and the new piece (it is most unlikely that the EXISTING service will have enough slack to be jointed to the new main)
Each new joint carries some risk of faults, including an open CNE. A new joint may be a greater risk than one that has survived for decades, at least until the initial failures in the new joints are discovered and dealt with. Though remember that each new joint that blows up probably requires at least TWO new joints for repairs.
I believe that all new DNO mains should be 4 core plus a separate earth.