lyledunn:
The Irish Regs (IS10101: 2020) on the other devote only 3/4 of a line; “In TN systems the final circuit supplying a connecting point shall be a TN-S system”. My understanding is that this regulation is not modified from HD 60364-722Edit; maybe if GK reads this he could confirm or otherwise that last sentence.
Confirmed, although the Clause number is 722.312.2.1, and the requirement is
In a TN system, the final circuit supplying a connecting point shall be a TN-S system.
Interestingly, in IEC/HD speak, this does not mean the supply arrangement has to be TN-S; there are many international standards, which have the notion that in a TN-C-S, downstream of the point of separation of the protective conductor is TN-S.
As an aside, this creates a unique situation in interpreting those standards which are not incorporated in BS 7671 in the UK. For example, does BS EN 60079-14 permit the electrical installation in a hazardous area to be derived from a TN-C-S (PME) system?
I would also add that, whilst the UK is presently the only country whose national wiring standard is concerned with the risks of broken neutrals in TN-C-S supply distribution arrangements, other countries are beginning to consider them, as we have seen with the recent discussion thread here.
... and finally, I understand for the rest of the UK, we are looking at a recorded average of just under 1 broken neutral event reported today, but the YoY rate of increase is perhaps more concerning. I have not seen specific data regarding damage to equipment or installations, injuries, or worse, just "events".
lyledunn:
The Irish Regs (IS10101: 2020) on the other devote only 3/4 of a line; “In TN systems the final circuit supplying a connecting point shall be a TN-S system”. My understanding is that this regulation is not modified from HD 60364-722Edit; maybe if GK reads this he could confirm or otherwise that last sentence.
Confirmed, although the Clause number is 722.312.2.1, and the requirement is
In a TN system, the final circuit supplying a connecting point shall be a TN-S system.
Interestingly, in IEC/HD speak, this does not mean the supply arrangement has to be TN-S; there are many international standards, which have the notion that in a TN-C-S, downstream of the point of separation of the protective conductor is TN-S.
As an aside, this creates a unique situation in interpreting those standards which are not incorporated in BS 7671 in the UK. For example, does BS EN 60079-14 permit the electrical installation in a hazardous area to be derived from a TN-C-S (PME) system?
I would also add that, whilst the UK is presently the only country whose national wiring standard is concerned with the risks of broken neutrals in TN-C-S supply distribution arrangements, other countries are beginning to consider them, as we have seen with the recent discussion thread here.
... and finally, I understand for the rest of the UK, we are looking at a recorded average of just under 1 broken neutral event reported today, but the YoY rate of increase is perhaps more concerning. I have not seen specific data regarding damage to equipment or installations, injuries, or worse, just "events".