Hi all, my father in law has a rental property that was completely rewired and with new split load CU five years ago. The installation is now due an inspection. Will the fact that the CU is plastic constitute a "fail"?
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
davezawadi (David Stone):
514.14.1 explicitly allows red and black to remain on previously installed cables, to earlier editions. Thus these do not require to be changed, although there should be a notice (no notice = C3).
Only if there are mixed colours - 514.14.1
davezawadi (David Stone):
Inspection to chapter 6, and therefore BS7671, are quite simple to follow given the correct qualifications and experience. If it inspects as safe, it matches BS7671 requirements for an electrical installation which is what the legislation requires. If it is a new installation it must exactly match, if existing then judgement of safety comes into play which is obviously not what you are attempting to apply to the CU for example