PAT Substitute Leakage Test

Hi.


Have a question on voltages and equipment regarding a PAT test option.

On some equipment, like motors, if the voltage drops below the minimum, damage can occur. In the case of motors, from overheating.

Not sure what the effect would be on electronics. I believe the inductive reactance may reduce like it would if the frequency went down. Not sure if it's the same case with voltage.

I was looking up PAT testers the other day. I did the C&G PAT course years ago and the last time I used PAT tester is about 15 years ago.

There is now an option to do a "Substitute leakage current test".

Depending on the tester it is between 60 & 100 volts.

I would have thought the only way to get leakage is for the equipment to be running and that would take full voltage.

I can't see how using a voltage so low will get a leakage result. I'm also wondering if there is any adverse effect on the equipment. I scanned through the Fluke manual and it didn't have any restrictions on the type of equipment.

I know they are unlikely to produce the tester with this test if it damaged equipment.

I'm theorising that even if equipment can get damaged if the voltage drops below the minimum, the test voltages that are much lower are not enough to run equipment so no damage can occur.

Still can't see how you can get a leakage result though.


Any thoughts?
Parents
  • The problem, lyledunn, with this is that given a class 2 device there is no obvious earth to test it to. Do you use the plastic housing, the hand of the guy holding it or stick a probe into the ground somewhere?

    I'd agree with the above comments that it's probably not a suitable test for a Class II appliance for an in-service test. Where insulation or similar tests are done on Class II appliances for things like type testing I understand that they'd wrap accessible bits of the appliance in foil which is then Earthed (at least in the sense of being connected to the "earth" terminal of the test meter) - and likely placed on an insulating surface, and if necessary any trigger being held in by mechanical means. Probably way beyond reasonable for a routine in-service test.


       - Andy.
Reply
  • The problem, lyledunn, with this is that given a class 2 device there is no obvious earth to test it to. Do you use the plastic housing, the hand of the guy holding it or stick a probe into the ground somewhere?

    I'd agree with the above comments that it's probably not a suitable test for a Class II appliance for an in-service test. Where insulation or similar tests are done on Class II appliances for things like type testing I understand that they'd wrap accessible bits of the appliance in foil which is then Earthed (at least in the sense of being connected to the "earth" terminal of the test meter) - and likely placed on an insulating surface, and if necessary any trigger being held in by mechanical means. Probably way beyond reasonable for a routine in-service test.


       - Andy.