Sparkingchip:
Are you still using the original electrician or is this another one that has become involved?
Heh, I wondered if someone from my other post would comment. This is the same EICR. There are four observations in total:
1. Lighting circuits have little or no earth : C1
2. No back boxes on lighting circuit : C2
3. No earth bond to some socket boxes : C2
4. Water and Gas bonded but not found : C3
Obviously 1. concerned me the most because C1 implies "Danger present. Risk of injury." The others I want to address. 2. I've addressed by the actions I describe in the other post (nylon screws, plastic pattress boxes). 3. I suspect is down to lack of earth tail inside the box, but the screws are earthed so the back box is earthed. Hence this post.
4. I'm not worried about - the two are bonded under the floorboards near the CU. I will add another, more visible wire, when I rewire.
Sparkingchip:
Are you still using the original electrician or is this another one that has become involved?
Heh, I wondered if someone from my other post would comment. This is the same EICR. There are four observations in total:
1. Lighting circuits have little or no earth : C1
2. No back boxes on lighting circuit : C2
3. No earth bond to some socket boxes : C2
4. Water and Gas bonded but not found : C3
Obviously 1. concerned me the most because C1 implies "Danger present. Risk of injury." The others I want to address. 2. I've addressed by the actions I describe in the other post (nylon screws, plastic pattress boxes). 3. I suspect is down to lack of earth tail inside the box, but the screws are earthed so the back box is earthed. Hence this post.
4. I'm not worried about - the two are bonded under the floorboards near the CU. I will add another, more visible wire, when I rewire.