New EICR - "No earth bond to some socket boxes: C2"?

Former Community Member
Former Community Member
I have a new EICR which has the observation "No earth bond to some socket boxes: C2".


I have checked continuity between all faceplate mounting screws and the earth of the socket. They are all connected, i.e. the back box is at least earthed by the screw if not with a tail internally (I have not removed the front plates of any sockets). The earth of each socket is connected to the ring.


While it is best practice, is it a requirement of the regulations that a tail is connected internally?


many thanks



Parents
  • True, it’s cross section rather than area.


    And of course, if it is a healthy ring the CPC is doubled up.


    But you can find  the single cable of a 2.5/1.0 twin and earth socket ring circuit “spur” quite legitimately wired directly into the fuse holder protected by a 30 amp fuse wire.
Reply
  • True, it’s cross section rather than area.


    And of course, if it is a healthy ring the CPC is doubled up.


    But you can find  the single cable of a 2.5/1.0 twin and earth socket ring circuit “spur” quite legitimately wired directly into the fuse holder protected by a 30 amp fuse wire.