Sparkingchip:
>>>
If you are doing testing for an EICR and you find a rewirable fuse board, a high PSC and 2.5 mm twin and earth with 1.0 mm all sorts of potential issues should be flagged up, because the earth conductor is only 0.15 mm bigger than the fuse wire.
Andy Betteridge
Not quite as bad as that - the 0.85mm dia wire is not 0.85mm2 cross-section; more like 3/4 of that (0.57mm2 to be exact) So the energy per unit length will be 57%, and the adiabatic temperature rise (as not only is there less power, there is more volume of metal to heat ) will be 57% of 57%, or 0.32. So if the 0.85mm diameter fuse wire reaches 1100C and melts, the CPC reaches something more like 340C and in that fraction of a second before it start to cool, it damages the surface of the PVC on either side of it. Not great, as the cable insulation will eventually fail, but not likely to lead to the big danger of the CPC blowing open and the fuse remaining undamaged.
Of course there is precious little margin if that 1mm cpc is nicked or strained at some point, and repeated firing of a fuse in rapid succession may blow the CPC clear eventually.
UKPN:
What surprises me is why this guy is still on here asking questions on codes that were supposed to be remedied within 28 days ago. and the local council notified. Putting aside he has employed an amateur electrician who doesnt know a C2 from a Fi, and these "defects" didnt need modifying anyway, why hasnt the "inspector" fixed the "potentially dangerous" installation? Alternatively, why not employ a real electrician? Whats next? The forum waits.
Regards, UKPN
IMO the codes have been remedied within 28 days.
Who would be responsible for notifying the council, the electrician issuing the certificate?
JPCoetzee:UKPN:
What surprises me is why this guy is still on here asking questions on codes that were supposed to be remedied within 28 days ago. and the local council notified. Putting aside he has employed an amateur electrician who doesnt know a C2 from a Fi, and these "defects" didnt need modifying anyway, why hasnt the "inspector" fixed the "potentially dangerous" installation? Alternatively, why not employ a real electrician? Whats next? The forum waits.
Regards, UKPNIMO the codes have been remedied within 28 days.
Who would be responsible for notifying the council, the electrician issuing the certificate?
No, it seems to be the landlord.
UKPN makes a good point.
I think that one has to do one of two things: (1) get it fixed by a "qualified person" who will certify in writing that the work has been done; or (2) get it fixed by anybody else and then get a new EICR which demonstrates that the installation is safe for continued service.
JPCoetzee:UKPN:
What surprises me is why this guy is still on here asking questions on codes that were supposed to be remedied within 28 days ago. and the local council notified. Putting aside he has employed an amateur electrician who doesnt know a C2 from a Fi, and these "defects" didnt need modifying anyway, why hasnt the "inspector" fixed the "potentially dangerous" installation? Alternatively, why not employ a real electrician? Whats next? The forum waits.
Regards, UKPNIMO the codes have been remedied within 28 days.
Who would be responsible for notifying the council, the electrician issuing the certificate?
Under Section 3 of The Electrical Safety Standards in the Private Rented Sector (England) Regulations 2020, the landlord is responsible for obtaining all the required paperwork, and notifying anyone who needs to be notified. That would be completely separate from any notification under Building Regulations, which is often done by the electrician.
https://www.legislation.gov.uk/uksi/2020/312/regulation/3/made