522.6.203 RCD protection required for cables in metal stud walls, what about ceilings?

c7060d8203d5c0b63eb16e6978c26b10-huge-22ce4495-f508-46da-b2d6-1820c53c611a.jpg
Parents
  • Sparkingchip:

    The one flat I moved the lighting to the RCD protected side of the consumer unit, in the other I swapped the main switch out for a RCD, a quick fix in both flats.


    So both flats now have all their circuits protected by a RCD removing several  observations and codes from the EICR.


    I won’t be able to do something like that every time, so some will have to be coded.


    Make a determination.


    Andy Betteridge  




    ​​​​​Trying to balance risk of danger from livened up metal parts and risk of danger and inconvenience from all ccts on one RCD: perhaps not an easy choice to make while also factoring in cost.


Reply
  • Sparkingchip:

    The one flat I moved the lighting to the RCD protected side of the consumer unit, in the other I swapped the main switch out for a RCD, a quick fix in both flats.


    So both flats now have all their circuits protected by a RCD removing several  observations and codes from the EICR.


    I won’t be able to do something like that every time, so some will have to be coded.


    Make a determination.


    Andy Betteridge  




    ​​​​​Trying to balance risk of danger from livened up metal parts and risk of danger and inconvenience from all ccts on one RCD: perhaps not an easy choice to make while also factoring in cost.