522.6.203 RCD protection required for cables in metal stud walls, what about ceilings?

c7060d8203d5c0b63eb16e6978c26b10-huge-22ce4495-f508-46da-b2d6-1820c53c611a.jpg
Parents
  • Metal stud partitions do not require earthing, cables in them require 30 mA RCD protection.


    701.401.3.6 distinguishes between serving the location and zones within a bathroom, in a bathroom or shower room you need 30 mA RCD protection for circuits:

    (i) serving the location 

    (ii) passing through zones 1 and/or 2 not serving the location.


     Andy B.
Reply
  • Metal stud partitions do not require earthing, cables in them require 30 mA RCD protection.


    701.401.3.6 distinguishes between serving the location and zones within a bathroom, in a bathroom or shower room you need 30 mA RCD protection for circuits:

    (i) serving the location 

    (ii) passing through zones 1 and/or 2 not serving the location.


     Andy B.