522.6.203 RCD protection required for cables in metal stud walls, what about ceilings?

c7060d8203d5c0b63eb16e6978c26b10-huge-22ce4495-f508-46da-b2d6-1820c53c611a.jpg
Parents
  • The main issue with metal stud partition walls is someone like me - the installer - When I want to install a new switch or socket because I've created a meeting room in an office space that was open plan - what do I do?


    I get my 25mm hole saw - or others may get a 10mm drill and poke my head above the ceiling and drill down into the wall. Install lighting cable. I used to use SWA and now use BS8436 but I've often seen twin and earth dropped down to the switch. 


    If I want a new socket - I drill upwards from the floor with a 90' drill (I'd always use a 25mm hole saw but its common to see a 10mm drill having been used - and there's no way to fit mechanical protection to that hole. - In a completed plaster board wall and you're installing a socket at some future point)


    I always use BS8436 on a B type MCB now - used to use SWA - but its common again - to see twin and earth being use streight off the underfloor non RCD protected underfloor bus bar. 


    Hence - I've always reasoned - why that reg came to be.................
Reply
  • The main issue with metal stud partition walls is someone like me - the installer - When I want to install a new switch or socket because I've created a meeting room in an office space that was open plan - what do I do?


    I get my 25mm hole saw - or others may get a 10mm drill and poke my head above the ceiling and drill down into the wall. Install lighting cable. I used to use SWA and now use BS8436 but I've often seen twin and earth dropped down to the switch. 


    If I want a new socket - I drill upwards from the floor with a 90' drill (I'd always use a 25mm hole saw but its common to see a 10mm drill having been used - and there's no way to fit mechanical protection to that hole. - In a completed plaster board wall and you're installing a socket at some future point)


    I always use BS8436 on a B type MCB now - used to use SWA - but its common again - to see twin and earth being use streight off the underfloor non RCD protected underfloor bus bar. 


    Hence - I've always reasoned - why that reg came to be.................