gkenyon:Chris Pearson:
Can it ever be PME if there is only one earth rod?Yes - at the very least PNB. See G12/4, Clause 4.11. The reason PME conditions apply if there is only one electrode is that there can be fortuitous electrodes such as extraneous-conductive-parts. Since up to 4 customers can be supplied with the arrangement, diverted neutral currents can flow through these ...
This seems to be the operative sentence:
Earth terminals provided using PNB shall be treated in all respects as PME earth terminals.
AJJewsbury:
In my head, PNB clearly can never be PME - any system has a certain number of points where the N is deliberately earthed - if it's one it cannot be PME, if it's greater than one it cannot be PNB. The definitions do not overlap.
gkenyon:Chris Pearson:
Can it ever be PME if there is only one earth rod?Yes - at the very least PNB. See G12/4, Clause 4.11. The reason PME conditions apply if there is only one electrode is that there can be fortuitous electrodes such as extraneous-conductive-parts. Since up to 4 customers can be supplied with the arrangement, diverted neutral currents can flow through these ...
This seems to be the operative sentence:
Earth terminals provided using PNB shall be treated in all respects as PME earth terminals.
AJJewsbury:
In my head, PNB clearly can never be PME - any system has a certain number of points where the N is deliberately earthed - if it's one it cannot be PME, if it's greater than one it cannot be PNB. The definitions do not overlap.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site