Chris Pearson:
Can it ever be PME if there is only one earth rod?
Yes - at the very least PNB. See G12/4, Clause 4.11. The reason PME conditions apply if there is only one electrode is that there can be fortuitous electrodes such as extraneous-conductive-parts. Since up to 4 customers can be supplied with the arrangement, diverted neutral currents can flow through these ...
lyledunn:
As I understand it, PME describes a specific method of providing a consumers earth. TNCS is an earthing arrangement that includes the PME terminal but extends in to the installation to additionally describe the relationship between neutral and earth therein.
There can be TN-C-S without PME arrangements or conditions, but not, at least in the UK, where the supply is provided to the consumer at LV, and the provisions of the ESQCR apply.