PME vs TN-C-S

Are PME and TN-C-S supplies exactly the same?  Or does PME also have requirements regarding the number and relative location of suppliers earthing rods?

I am thinking here where the DNO replaces a length of failed 4-core (3-phase + Neutral) PILC cable with Wavecon or similar cable which has a combined Neutral and Earth conductor.  The average consumer would not know that their electricity supply's method of earthing had been changed.

Clive.
Parents
  • I’ll go for:

    2 or more DNO earths = PME protective multiple earthing.

    1 DNO earth = PNB protective neutral bonding.

    Both are TN-C-S combined in the DNO network and separate in the consumers installations. 

Reply
  • I’ll go for:

    2 or more DNO earths = PME protective multiple earthing.

    1 DNO earth = PNB protective neutral bonding.

    Both are TN-C-S combined in the DNO network and separate in the consumers installations. 