PNB is also (most of the time) PME in a public distribution network,
gkenyon:Chris Pearson:
Can it ever be PME if there is only one earth rod?Yes - at the very least PNB. See G12/4, Clause 4.11. The reason PME conditions apply if there is only one electrode is that there can be fortuitous electrodes such as extraneous-conductive-parts. Since up to 4 customers can be supplied with the arrangement, diverted neutral currents can flow through these ...
This seems to be the operative sentence:
Earth terminals provided using PNB shall be treated in all respects as PME earth terminals.
AJJewsbury:
In my head, PNB clearly can never be PME - any system has a certain number of points where the N is deliberately earthed - if it's one it cannot be PME, if it's greater than one it cannot be PNB. The definitions do not overlap.