0.8% were found to be dangerous (C1), 19.6% Potentially Dangerous (C2) and 25.6% requires improvement (C3).
OK, there is a possibility of an earth fault on the EV charger at the same time as a loss of neutral on the supply and someone touching a lamppost and the car at the same time, but this applies whether it is an EV charger or my vacuum cleaner while I'm cleaning the car.
John Peckham:
With a loss of the supply neutral the vehicles bodywork will rise up to a voltage possibly approaching 400V
Just to reinforce this ... it's not as simple as considering that the Neutral downstream of the broken PEN conductor can only "float" up to the highest phase to earth voltage.
If one phase is lightly loaded, and the other two phases have roughly equal loads, but opposing power factors, the voltage can rise above the phase to Earth voltage - the worst-case being nearly 1.4U, where U represents the actual supply voltage to Earth. Worth remembering that the worst-case value of U may not be 253 V for many LV transformers in the UK, but 264 V.
UKPN:
Am I the only person who thinks this is an utter disgrace?
You will be John until you pass us the evidence.
C1, C2, C3, Apparently Another code of practice, let's see the evidence, John. Most likely DNO PME fails, because if the installs were simple TT, there would be no problem.
Here is a press release from ECA.
It seems that the whole EVCP installation from service head to the charge point itself was audited. It also accepts that there were some false "positives". What we are not told is where the inadequacies were.
132.16 and 644.1.2 should ensure that the installation is inspected and tested all the way from the service head to the EVCP, but I suspect that in reality it starts from the garage CU in plenty of cases.