Chris 223:
Chris, your description is more or less the scenario. Only difference is that there are separate MDBs for power and lighting and as such, the grouping factor would be 0.5 and end up with the rating of the home run to be 16A. Is it ok to use the estimated design current for sockets?
I can not argue with those calculations. What you haven't mentioned (and may be a commercial confidence) is what will be plugged into the sockets. By their very nature, sockets imply diversity - they do not have the same 13 A load plugged in 24/7! As David has mentioned, the grouping factor is based upon fully loaded circuits. I think that diversity will allow you to get away with 20 A OCPDs or even 32 A ones.
The reference is 311.1.
Harry Macdonald:
You really do need to know who will do what with your sockets.
A number of years ago I was involved with a certain Opera House. At the end of the Commissioning of the systems we needed to test the air-conditioning at full load, i.e. simulate the heat given off by 2000+ seated people.
We did this by having a large number of 3kW fan heaters as well as some strings of 100W lamps distributed around the auditorium.
I suspect the diversity calculations didn't allow for all available ring mains to be fully loaded for several hours.
At the back of my mind is a figure of 100 W for a person, so that would be 200 kW. Wow!