BS 8519

Hello,


I understand that the standard identifies the need for a dedicated containment for the fire rated life safety circuits. I assume this is so the normal circuits (non fire rated) will not compromise the integrity of the life safety circuits in case of fire (eg normal circuits will be on fire before the fire rated circuits which will be next to them if they were installed on the same containment).


But wouldn’t the same happen with the cpcs of the life safety circuits that are not fire rated?


Furthermore, is it ok to install on the same containment a circuit with 30 mins fire survival time (eg fire alarms) along with a circuit of 1 or 2h fire survival time (eg disabled refuge)?


I was under the impression that the fire survival time of a circuit is based on its wickest component but this does not always seem to be the case since the cpc are installed in the same containment.


It would be appreciated if you could share your thoughts.
Parents
  • Morning Chris


    This is a very complicated subject. Spookily I am working on a presentation at the moment for an IET Webinar.  The target date is November 17th and in the same session another IET member is going to be doing Emergency lighting.


    Every LSS installation will be different depending on the fire strategy for the building. Both the primary circuits and the secondary circuits need to be fire rated cables  and run in diverse routes through the building with fire separation. 


    That is a taster for the show coming to you in the near future.
Reply
  • Morning Chris


    This is a very complicated subject. Spookily I am working on a presentation at the moment for an IET Webinar.  The target date is November 17th and in the same session another IET member is going to be doing Emergency lighting.


    Every LSS installation will be different depending on the fire strategy for the building. Both the primary circuits and the secondary circuits need to be fire rated cables  and run in diverse routes through the building with fire separation. 


    That is a taster for the show coming to you in the near future.