BS 8519

Hello,


I understand that the standard identifies the need for a dedicated containment for the fire rated life safety circuits. I assume this is so the normal circuits (non fire rated) will not compromise the integrity of the life safety circuits in case of fire (eg normal circuits will be on fire before the fire rated circuits which will be next to them if they were installed on the same containment).


But wouldn’t the same happen with the cpcs of the life safety circuits that are not fire rated?


Furthermore, is it ok to install on the same containment a circuit with 30 mins fire survival time (eg fire alarms) along with a circuit of 1 or 2h fire survival time (eg disabled refuge)?


I was under the impression that the fire survival time of a circuit is based on its wickest component but this does not always seem to be the case since the cpc are installed in the same containment.


It would be appreciated if you could share your thoughts.
  • Morning Chris


    This is a very complicated subject. Spookily I am working on a presentation at the moment for an IET Webinar.  The target date is November 17th and in the same session another IET member is going to be doing Emergency lighting.


    Every LSS installation will be different depending on the fire strategy for the building. Both the primary circuits and the secondary circuits need to be fire rated cables  and run in diverse routes through the building with fire separation. 


    That is a taster for the show coming to you in the near future.
  • Former Community Member
    0 Former Community Member
    Generally, the reason for separate containment is that all and sundry messing about with non safety systems aren't likely to damage life safety cabling - although correctly you do need to consider the interaction hazard between systems.


    CPC's aren't specifically a worry per se - to melt the conductor needs temperatures way beyond the fire rating of the cable - and basically a bit of copper with all the sheathing burnt off, is still an effective CPC.


    There is usually no issue with BS 5839  life safety systems of differing fire resistance sharing containment - but in your example, it should raise an eyebrow as to why the fire detection and alarm is only a 30 minute system, when the refuges are a 120 minute system - one would imagine a facility needing refuge comms would also need an enhanced grade on the Part 1 system to reflect the rating on the Part 9 system.


    What you shouldn't do is mix non BS 5839 systems with other systems eg, it's not appropriate to run fire and emergency lighting on the same containment (as both relevant standards advise against it for the reasons given in my first comment


    Regards


    OMS

  • Hi John, it sounds interesting. I have read both 2010 & 2020 versions along with BS 9999 and others, but I think i still have some queries that I m not able to find a clear way forward (only about details). Ideally, the respective project fire strategy/engineer should be providing the answer but unfortunately in the real world you dont always get what is required.


    OMS, thanks a lot for your response. Appreciated as always.
  • What you shouldn't do is mix non BS 5839 systems with other systems eg, it's not appropriate to run fire and emergency lighting on the same containment (as both relevant standards advise against it for the reasons given in my first comment




    Not questioning your wisdom, but how far does this go?

    I regularly see recent commercial refits with fire cabling cable tied to one side of a basket, and final circuits tied to the other half , with no physical separation barriers. There are also the ones with the clip in metal dividing inserts to divide the basket, and, then those with a separate basket for fire cabling, but using the same hangers/brackets to hold them.

    What is 'the same containment'? 

    By that, I would expect to have a separate basket for the fire cabling, but many installs think they can use the same basket, so long as the cabling is around 30-50mm apart from the final circuits.


  • Former Community Member
    0 Former Community Member
    Well I guess BS 5839 is quite clear regarding "separate" and the commentary suggests that it's to prevent damage to fire systems (or emergency lighting systems) which may be caused by all and sundry playing around with the "other systems" sharing that containment.


    Sure, you see all kinds of attempts to "circumnavigate the requirements" by using a bit of space, by using a bit of a divider etc, but I would view all of those practices as "non compliant" with BS 5839 (or BS 7671).


    I would have less of an issue with a properly designed (and appropriately spaced) common containment "gallery" - typically ladder brackets (M10 drop rods and unistrut) on several levels, containing (say) Main LV power trays/ladders. Voice and data baskets. BMS or other EC&I containment, local small power and lighting containment, fire alarm containment etc


    I appreciate that isn't exactly how the commercial market sees things


    Regards


    OMS


  • I think the idea of seperate containment is/can be a problem.

    A tray with dividers - are the divisions seperate containers? well the 2,3,4 channels might be but the overall trough isn`t.

    There again completely seperate trays held by the same struts etc could be just as onerous.

    Taking it further to another (silly) conclusion, a whole area/room/building is a "container".

    You need to not only read the particulare reg(s) but also it`s intention of how far we mitigate risks
  • My understanding is that life safety supplies should be on a separate cable support system which ideally would be installed above all other services so a premature collapse of the later would not compromise/destroy the life safety circuits.


    But if the spirit of the reg is that sundries of normal circuits might affect the life safety circuits then maybe a neat installation with dividers could be enough?
  • I suspect that this is an area where we need to read the BS very carefully. I have BS5266 - 1999 to hand, so I may be out of date, but this talks a lot about separation, then says that if such separation is not provided MICC can be used, and then says "equally acceptable would be any cable complying with BS6387 ...".

    Perhaps someone can read the current versions carefully to see if this is still the situation.