What you shouldn't do is mix non BS 5839 systems with other systems eg, it's not appropriate to run fire and emergency lighting on the same containment (as both relevant standards advise against it for the reasons given in my first comment
Not questioning your wisdom, but how far does this go?
I regularly see recent commercial refits with fire cabling cable tied to one side of a basket, and final circuits tied to the other half , with no physical separation barriers. There are also the ones with the clip in metal dividing inserts to divide the basket, and, then those with a separate basket for fire cabling, but using the same hangers/brackets to hold them.
What is 'the same containment'?
By that, I would expect to have a separate basket for the fire cabling, but many installs think they can use the same basket, so long as the cabling is around 30-50mm apart from the final circuits.
What you shouldn't do is mix non BS 5839 systems with other systems eg, it's not appropriate to run fire and emergency lighting on the same containment (as both relevant standards advise against it for the reasons given in my first comment
Not questioning your wisdom, but how far does this go?
I regularly see recent commercial refits with fire cabling cable tied to one side of a basket, and final circuits tied to the other half , with no physical separation barriers. There are also the ones with the clip in metal dividing inserts to divide the basket, and, then those with a separate basket for fire cabling, but using the same hangers/brackets to hold them.
What is 'the same containment'?
By that, I would expect to have a separate basket for the fire cabling, but many installs think they can use the same basket, so long as the cabling is around 30-50mm apart from the final circuits.