Conductor repair

Former Community Member
Former Community Member
I have come across an socket outlet which has had the insulation on a neutral wire repaired with heat shrink, it looks like the socket screw has damaged it previously.
Would this be an acceptable repair?
Parents
  • if the heatshrink is just making good scuff damage to the core insulation, in  a place where single insulation would be expected - i.e in the back box, then that is fine. If the damage is so bad that  it is hiding a badly mangled copper core then  it would not be OK.

    In short the technique is perfectly OK, but it needs to have been properly done. If it feels lumpy like a core  has come out or has a  limp 'broken bone' feel to it, the wire needs to be cut and joined .
Reply
  • if the heatshrink is just making good scuff damage to the core insulation, in  a place where single insulation would be expected - i.e in the back box, then that is fine. If the damage is so bad that  it is hiding a badly mangled copper core then  it would not be OK.

    In short the technique is perfectly OK, but it needs to have been properly done. If it feels lumpy like a core  has come out or has a  limp 'broken bone' feel to it, the wire needs to be cut and joined .