Or a PHASE CURRENT & LINE CURRENT result of 7.53A if 3000W is entered (which I understand would be the Wattage per phase)
How did you manage to come up with that figure? 3000 / 230 = 13.04. (Which is why we have 13A sockets in the UK). A 9000W wye element is really just three 3000W single phase elements, one per phase.
Why would this be the case?
What is TT earthed?
I'm not sure what to say, Dan, I simply don't get those results when I use the calculator - see attached screenshots.
3. According to BS7671:2018 554.1.2, "The supply to the electrode water heater or electrode boiler shall be controlled by a linked circuit-breaker arranged to disconnect the supply from all electrodes simultaneously and provided with an overcurrent protective device in each conductor feeding an electrode.". I would interpret this as needing a 3P breaker.