This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

ADS

Former Community Member
Former Community Member
How exactly does ADS work?
Parents
  • Coby:

    There is nothing incorrect about my last post; and you have still not explained how ADS works without EEB.


    In a house without a metal frame, and with only plastic internal and external service pipes, there is no equipotential bonding.


    ADS still operates in the manner I have explained. It relies on the fault current path back through the protective conductor of the circuit concerned, not the equipotential bonding.


    Equipotential bonding does not affect the speed of operation of protective devices in ADS (as far as BS 7671 calculations are concerned) - it is used only to control touch voltages for the duration of a fault.


Reply
  • Coby:

    There is nothing incorrect about my last post; and you have still not explained how ADS works without EEB.


    In a house without a metal frame, and with only plastic internal and external service pipes, there is no equipotential bonding.


    ADS still operates in the manner I have explained. It relies on the fault current path back through the protective conductor of the circuit concerned, not the equipotential bonding.


    Equipotential bonding does not affect the speed of operation of protective devices in ADS (as far as BS 7671 calculations are concerned) - it is used only to control touch voltages for the duration of a fault.


Children
No Data