davezawadi (David Stone):
The interesting effect is that the leakage seems to cause an increase in trip time, rather than a failure to trip when using my MFT to test.
Smoking gun? Increase in trip time could well mean not tripping in a time (for additional protection) that saves someone's life. The trip times for RCDs are based on roughly a P90 demographic ("protects about 90 %") of adults.
Of course, with most MFT it's perhaps not possible to generate a fault of negligible impedance (resulting in the machine recording a trip time) downstream of the rectifier's output? If I can think of a way of doing this, I'll post back on that.
I have spent a couple of hours yesterday experimenting with RCDs, rectifiers, and various degrees of leakage from the rectifier DC to Earth. The interesting effect is that the leakage seems to cause an increase in trip time, rather than a failure to trip when using my MFT to test. A different RCD tester shows much less effect although they both give similar results with a normal unloaded circuit and RCD. I am using a 1kW lamp load on the rectifier output, so the RCD transformer is actually having to do some work, rather than the unloaded condition. This is an attempt to demonstrate a real circuit rather than the unusual test condition of zero load.
5k resistance increases trip time to a second or so, but does no prevent a trip.
Of course, with most MFT it's perhaps not possible to generate a fault of negligible impedance (resulting in the machine recording a trip time) downstream of the rectifier's output?
The comment about additional protection from Andy is a point, but how does a person contact anything inside the boiler, an Earthed metal box?
AJJewsbury:
I think the worry about additional protection is that the boiler could remove additional protection from everywhere downstream of the RCD - so picture nail into a cable upstream of the boiler (or elsewhere in the house if the RCCB is covering many circuits) and additional protection might be ineffective.
I see three issues:
(1) The boiler, or at least it's DC modulating pump will trip a type AC RCD in normal use. I assume the electronics are rather like the front half of a VSD, so that is perfectly possible. That would be obvious during commissioning.
(2) A fault in the boiler might not trip a type AC RCD. I think that we have covered that one. If the boiler does not require RCD protection, then this possibility isn't a problem.
(3) The boiler might blind an RCD, either in normal use, or under some fault condition which does not trigger ADS.
I have asked Schneider whether their type AC RCDs are compatible with DC modulating pumps and I have asked Worcester to explain - i.e. to answer my original question.
All this does seem to be a bit beyond the call of duty. Perhaps the householder should have told the plumber to fit a boiler which can cope with a type AC RCD? ?