davezawadi (David Stone):
Very well, Gentlemen, the boiler manufacturer cannot be bothered to correctly fuse his appliance, expects there to be faults in his electronics, safety coverings, etc. and so we must fit a type A RCD.
Selectivity springs to mind here.
The manufacturer's instructions apparently (according to earlier post) say that where an RCD is required for additional protection ... not protection.
I guess the poor manufacturer can't win? Some people ask "How on earth can I tell which RCD to use?" - yet others berate them for helping out and clearly stating that?
I think it would be reasonable for someone to describe what fault exactly could require a type A RCD.
We can't go assuming the manufacturer has got it wrong just because it means the job is a little more difficult.
davezawadi (David Stone):
Hi Graham
Figure A53.1 shows waveforms which may cause some RCDs difficulties. We discussed those at length above. However, that was not the question I asked which was (written more clearly perhaps) "How can any credible fault produce those waveforms, and if it can, will it operate various types of RCD?" which is very different. I can always say "We need to provide additional protection of the highest level for safety" but that is not the correct answer at all, although it smacks of the usual British Gold plating of any possible regulation or even idea. I am interested in Credible faults that could occur, and once one is established, how often could it happen, in other words, the normal risk assessment criterion. It is unacceptable to expect to make everything completely zero risk, although some like to try and do so, particularly when it costs them nothing or worse when it makes them a profit!
Kind regards
David
No, David, Figure A53.1 shows faults that can and do occur downstream of the particular rectification or control arrangement shown - have a look at the diagram in Column 1, which shows the point of fault (effectively downstream of that point), and the fault waveform. The problem with half-wave rectified mains is it contains complex components, as I'm sure you're aware.
So, where could these faults occur? Some examples include:
I've been pondering the mention of additional/supplementary protection - presumably against direct contact - so we're expecting the RCD to see a residual current that's just flowing though a person who I presume is a fair approximation to a simple resistor so we shouldn't expect any waveform distortion or d.c. components on that score - so in that respect AC type RCDs should be adequate. On the other hand we have a load that might draw distorted waveform current for its normal load - so the RCD will see distorted a.c. load current plus pure sinewave shock current flowing out in its L coil, and just the distorted N return (without the shock current) in its N coil - so the question is: can we be sure that all AC type RCDs can spot a pure sinewave residual current when both the L and N load currents equally are distorted? I.e. does the insensitivity to distorted sinewaves occur before or after summing in the toroid?
- Andy.
Yes, whilst 10 mA and 30 mA RCDs are used for additional protection (perhaps a fault through a person), they may already be subject to complex components in residual currents downstream, and effectively "blinded" by that.
The situation with fault protection using RCDs is a little more complicated - because the fault may well be as described in A53.1.
It's also worth considering the wording in, say, some of the Part 7 sections - is the RCD providing additional protection or fault protection? Some Part 7's say "shall be protected by an RCD" - without mention of either fault protection or (in the cases where 30 mA RCDs) additional protection, or even protection against fire! Some clue may be available from the numbering of the requirements (i.e. considering which of the General Requirements in Parts 3, 4, 5, 6, or (in the case of AMD 2 DPC) 8.
AJJewsbury:
I've been pondering the mention of additional/supplementary protection - presumably against direct contact - so we're expecting the RCD to see a residual current that's just flowing though a person who I presume is a fair approximation to a simple resistor so we shouldn't expect any waveform distortion or d.c. components on that score - so in that respect AC type RCDs should be adequate. On the other hand we have a load that might draw distorted waveform current for its normal load - so the RCD will see distorted a.c. load current plus pure sinewave shock current flowing out in its L coil, and just the distorted N return (without the shock current) in its N coil - so the question is: can we be sure that all AC type RCDs can spot a pure sinewave residual current when both the L and N load currents equally are distorted? I.e. does the insensitivity to distorted sinewaves occur before or after summing in the toroid?
That is a pretty fair summary. In other words, might a fault in the boiler "blind" a type AC RCD?
The manufacturer's instructions don't require that this particular boiler be RCD protected so in a TN installation, ADS should provide shock protection for a fault inside it. Whether or not a distorted load current would trip a type AC RCD becomes irrelevant. So that leaves a fault in the supply cable (which need not require additional protection) or in the many cables which control the heating system, which are buried in walls < 50 mm from the surface, and which I assume are at mains voltage.
So to my mind, it is all about blinding. I await a response from the manufacturer.
Chris Pearson:
ADS should provide shock protection for a fault inside it.
So to my mind, it is all about blinding. I await a response from the manufacturer.
Well, yes ... selectivity? ADS may well not operate for faults of a few mA to Earth ... which in themselves are not always particularly dangerous of course, especially if they are "mapped" onto the Neutral because of an N-E fault from an ELV source with a voltage low enough not to drive that current through the human body.. but we know this might be sufficient to affect the operation of an upstream Type AC RCD ...