EICR Codes help for new Landlord.

Former Community Member
Former Community Member
Hi. I hope you are all well and keeping busy in these strange times. I look after a ladies house who has had to move back abroad and now needs to let the property out and so she has had an EICR done which has come back with saying it needs a total rewire for few grand. 


What I want to know is can I ask info on here about the codes he has put and if reasonable.


I don't won't to upset anyone by second guessing another trades persons work but I would like an idea if this is right or not?


Thanks you


Regards Lee
Parents
  • Oh deary me!


    3.3 How could the absence of a label possibly be C2?


    4.18 I assume that this is a TN installation so RCD is for additional and not fault protection.


    5.13 This is domestic, not industrial.


    Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2). Where have the R1+R2 figures come from in respect of the socket circuits when end to end tests appear to have been omitted? Could it be Zs - Ze? Insulation resistance is low for PVC cables and why test at 200 V?
Reply
  • Oh deary me!


    3.3 How could the absence of a label possibly be C2?


    4.18 I assume that this is a TN installation so RCD is for additional and not fault protection.


    5.13 This is domestic, not industrial.


    Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2). Where have the R1+R2 figures come from in respect of the socket circuits when end to end tests appear to have been omitted? Could it be Zs - Ze? Insulation resistance is low for PVC cables and why test at 200 V?