AJJewsbury:Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2).
That's 'cos they've decided that 5s disconnection times are appropriate for all the final circuits ?
It's complete nonsense (he said politely).
- Andy.
The entry for the maximum Zs is generated automatically after you enter the disconnection time, type and rating of the fuse or circuit breaker.
As I said above if you correctly complete the schedule of inspections the observations are entered ready for you to edit with references.
Use the software properly and you end up with a report in which everything tallies up and makes sense, unlike this one.
Andy B.
AJJewsbury:Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2).
That's 'cos they've decided that 5s disconnection times are appropriate for all the final circuits ?
It's complete nonsense (he said politely).
- Andy.
The entry for the maximum Zs is generated automatically after you enter the disconnection time, type and rating of the fuse or circuit breaker.
As I said above if you correctly complete the schedule of inspections the observations are entered ready for you to edit with references.
Use the software properly and you end up with a report in which everything tallies up and makes sense, unlike this one.
Andy B.