Mutley:
it needs a total rewire for few grand.
What I want to know is can I ask info on here about the codes he has put and if reasonable.
AJJewsbury:Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2).
That's 'cos they've decided that 5s disconnection times are appropriate for all the final circuits ?
It's complete nonsense (he said politely).
- Andy.
The entry for the maximum Zs is generated automatically after you enter the disconnection time, type and rating of the fuse or circuit breaker.
As I said above if you correctly complete the schedule of inspections the observations are entered ready for you to edit with references.
Use the software properly and you end up with a report in which everything tallies up and makes sense, unlike this one.
Andy B.
Sparkingchip:
You need to get an opinion from an electrician who can actually have a look at the installation, I don’t know what to suggest regards finding an electrician to do do. [sic]
Well I think that the owner is stuck between a rock and a hard place. There seems to be a sub-optimal EICR, but if she gets another one, why should it be any better and you still don't get around the no RCD no CPC lighting circuits.
On the other hand, the purpose of the new legislation is to safeguard tenants from these shoddy installations.
Being pragmatic, is the inspecting electrician prepared to remedy the issues highlighted above or can you get another electrician who would remedy what needs to be done (CU change?) and issue a satisfactory EICR?
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site