The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement

This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Assumed ambient temperature behind cooker? (Cable derating)

Hi,


I have a 40A cooker circuit (Type B RCBO). That would be borderline 6mm2 at <=40C ambient, 10mm2 at higher temperatures.


Does anyone have a rule of thumb for how warm it gets behind a free standing cooker? 40C is quite warm and modern devices are probably better insulated than older one.


Cheers :)


Tim
Parents
  • The ambient behind the cooker is unlikely to be anything like 40C. Now apply diversity to the circuit. Your cable will not even get more than a few degrees above ambient, whatever that is.
Reply
  • The ambient behind the cooker is unlikely to be anything like 40C. Now apply diversity to the circuit. Your cable will not even get more than a few degrees above ambient, whatever that is.
Children
No Data