Tri-Rated Wire Vs Equipment (Hook Up Wire)
Hi Guys
I have been designing hardware for electrical panels for many years now and generally have always used "TRI-RATED" wire within the enclosure, occasionally and more prevalent recently is the specification for Low Smoke Zero Halogen but what about Equipment Wire?
Has anybody used this within electrical control panels for 24Vdc control voltages, in what applications is this acceptable? I have seen machine builders use it often so therefore as they are following 60204 then is it also possible to use within Control Panels for machinery?
  • There is no issue with tri-rated for control panels etc. to the best of my knowledge.
    BS 7671 does not apply to assemblies, and a product standard would have to be followed in any case. BS EN 61439-series is the primary standard for switchgear/controlgear assemblies. If the control panels are for Machinery as defined in the Supply of Machinery (Safety) Regulations, then BS EN 60204-1 also applies.
  • Yes I have always used Tri-Rated wire and we would be following 60204/61439, it was more to see if anybody has used Equipment Wire within Control panels? And to see if there was any knowledge on when this is used and when it can cross into Control Gear?
  • Could you be more specific with your question? Controlgear comes under BS EN 61439 too? The use of this cable type in those applications seems to be very common ?
  • I suspect the OP is askiing about this kind of wire: https://uk.rs-online.com/web/p/hookup-equipment-wire/8606713/
  • Yes, I was not very detailed in that post.
    Tri-Rated Wire is generally known as BS6231 and Equipment Wire is generally known as UL1007.
    I have seen many uses of Equipment Wire but never specifically in control panels and I wonder why?
  • Equipment wire doesn't appear to be harmonized, so perhaps not as easy to incorporate by read-across to EU standards (for CE marking) of its certification ... similar to SY, CY, and YY, although in the case of SY, CY and YY, conductor and basic insulation conformity can perhaps be more easily addressed?
    Tri-rated is definitely harmonized, H05V2-K and H07V2-K.