TT system

In a TT system what protects the meter tails from an earth fault?
Parents
  • Sparkingchip:

    Plastic trunking.


    But according to the article you've linked to, the plastic trunking isn't required.

    "So, for meter tails or other insulated and sheathed cables, the basic insulation over the conductor and the non-metallic sheath are deemed to comply with the requirements for both basic and fault protection in Regulation 412.2 and hence don’t need to be installed in containment (unless required for mechanical protection)."


Reply
  • Sparkingchip:

    Plastic trunking.


    But according to the article you've linked to, the plastic trunking isn't required.

    "So, for meter tails or other insulated and sheathed cables, the basic insulation over the conductor and the non-metallic sheath are deemed to comply with the requirements for both basic and fault protection in Regulation 412.2 and hence don’t need to be installed in containment (unless required for mechanical protection)."