Sparkingchip:
Plastic trunking.
But according to the article you've linked to, the plastic trunking isn't required.
"So, for meter tails or other insulated and sheathed cables, the basic insulation over the conductor and the non-metallic sheath are deemed to comply with the requirements for both basic and fault protection in Regulation 412.2 and hence don’t need to be installed in containment (unless required for mechanical protection)."
Sparkingchip:
? No, they are not double insulated, they are insulated and sheathed
But ... they are considered to be ... in this particular case. The OP's question is clearly covered by Regulation 531.3.5.2.201
531.3.5.3.2.201 For Class I enclosures in TT systems where RCD protection is used on outgoing circuits, double or reinforced insulation of all live conductors (incoming cables, extension terminals, etc.) on the supply side of the incoming device, e.g. main switch, shall be used. Insulated and non-metallic sheathed cables are deemed to meet the requirements of double or reinforced insulation.
And, as others have already pointed out, this means that no other protection against contact with exposed-conductive-parts is necessary [to comply with BS 7671] because of this.