Neutral to earth on genny

Can I ask your opinion in relation to neutral /earth on this rather untidy changeover arrangement located just downstream of the main isolator? There are 2no 3-pole contractors with mains in bottom left and generator in bottom right. On the stud adjacent they have connected gen neutral, DNO neutral and installation earth. The arrangement means a self-imposed conversion to an unauthorised TNCS. I can’t be sure if the existing supply is already TNCS.
Parents
  • Former Community Member
    0 Former Community Member
    lyledunn:

    . I can’t be sure if the existing supply is already TNCS.


    Hi Lyle, if the main earthing arrangement is a code FI, is there any point in continuing the rest of an EICR? What limitations have been agreed prior to carrying out the inspection?


    Any other pics of the intake, generator etc may help?