lyledunn:
. I can’t be sure if the existing supply is already TNCS.
Hi Lyle, if the main earthing arrangement is a code FI, is there any point in continuing the rest of an EICR? What limitations have been agreed prior to carrying out the inspection?
Any other pics of the intake, generator etc may help?
lyledunn:
David, WB, I cannot give a C2 or FI as the report must have a satisfactory designation so such things must be rectified before the issue of the report.
I think it needs to be rectified - it's especially important if there's no earth electrode on the consumer side, but diverted neutral currents is a distinct possibility unless the premises is some distance from other installations and there are no shared extraneous-conductive-parts.