Can I ask your opinion in relation to neutral /earth on this rather untidy changeover arrangement located just downstream of the main isolator? There are 2no 3-pole contractors with mains in bottom left and generator in bottom right. On the stud adjacent they have connected gen neutral, DNO neutral and installation earth. The arrangement means a self-imposed conversion to an unauthorised TNCS. I can’t be sure if the existing supply is already TNCS.
Shows you how subjective these EICRs are. Here we have one top man on this forum saying “it’s probably not that dangerous” and another who is prepared to serve a Danger Notice.
perhaps Alan would be kind enough to expand on the dangers as he sees them?
David, WB, I cannot give a C2 or FI as the report must have a satisfactory designation so such things must be rectified before the issue of the report. I have a list of other things that fall into the C2 category for this particular installation. However, it seems to me that any given code should be accompanied by a clear indication of the reasons the call has been made along with a reference to at least the most pertinent regulation that has been breached.
Shows you how subjective these EICRs are. Here we have one top man on this forum saying “it’s probably not that dangerous” and another who is prepared to serve a Danger Notice.
perhaps Alan would be kind enough to expand on the dangers as he sees them?
David, WB, I cannot give a C2 or FI as the report must have a satisfactory designation so such things must be rectified before the issue of the report. I have a list of other things that fall into the C2 category for this particular installation. However, it seems to me that any given code should be accompanied by a clear indication of the reasons the call has been made along with a reference to at least the most pertinent regulation that has been breached.