Neutral to earth on genny

Can I ask your opinion in relation to neutral /earth on this rather untidy changeover arrangement located just downstream of the main isolator? There are 2no 3-pole contractors with mains in bottom left and generator in bottom right. On the stud adjacent they have connected gen neutral, DNO neutral and installation earth. The arrangement means a self-imposed conversion to an unauthorised TNCS. I can’t be sure if the existing supply is already TNCS.
Parents
  • Does the installation have its own earth electrode suitable for the generator when the supply is lost?
    • If it does have a suitable earth electrode, then it depends on whether the installation is PME as to whether danger is immediately possible
      • If it's already PME, and main bonding is suitably sized for that, then immediate danger is unlikely, It's a breach of legislation (if it's an LV supply under ESQCR and that should be noted) so there's a choice of C3 or FI - I'd go for the FI and reason being breach of legislation.

    • If it's not already PME, or bonding is not suitable, then the installation and service cable are susceptible to damaging  diverted neutral currents at any time - Code C2, or C1 if signs of overheating of any protective bonding conductors already. Again note possible breach of legislation - if bonding not suitable sized for PME, appropriate ref to Chapter 54.

       


    • It if does not have a suitable earth electrode, then I'd be tempted to go for C1, citing no suitable means of earthing for an intended mode of operation (mains loss could remove the link between N and/or supply means of earthing and Earth), ref Regulation 551.4.3.2.1. And again note possible breach of legislation.

Reply
  • Does the installation have its own earth electrode suitable for the generator when the supply is lost?
    • If it does have a suitable earth electrode, then it depends on whether the installation is PME as to whether danger is immediately possible
      • If it's already PME, and main bonding is suitably sized for that, then immediate danger is unlikely, It's a breach of legislation (if it's an LV supply under ESQCR and that should be noted) so there's a choice of C3 or FI - I'd go for the FI and reason being breach of legislation.

    • If it's not already PME, or bonding is not suitable, then the installation and service cable are susceptible to damaging  diverted neutral currents at any time - Code C2, or C1 if signs of overheating of any protective bonding conductors already. Again note possible breach of legislation - if bonding not suitable sized for PME, appropriate ref to Chapter 54.

       


    • It if does not have a suitable earth electrode, then I'd be tempted to go for C1, citing no suitable means of earthing for an intended mode of operation (mains loss could remove the link between N and/or supply means of earthing and Earth), ref Regulation 551.4.3.2.1. And again note possible breach of legislation.