Can I ask your opinion in relation to neutral /earth on this rather untidy changeover arrangement located just downstream of the main isolator? There are 2no 3-pole contractors with mains in bottom left and generator in bottom right. On the stud adjacent they have connected gen neutral, DNO neutral and installation earth. The arrangement means a self-imposed conversion to an unauthorised TNCS. I can’t be sure if the existing supply is already TNCS.
Parents
  • Looking further, something I did not realise


    The Electricity Safety, Quality and Continuity Regulations 2002 (ESQCR). ESQCR 2002 apply only to Great Britain. There is a separate legislative framework in Northern Ireland, the Electricity Safety, Quality and Continuity Regulations (Northern Ireland) 2012, that are enforced by HSENI


    from (here - a parliamentary question)

    Does anyone have a list of differences
Reply
  • Looking further, something I did not realise


    The Electricity Safety, Quality and Continuity Regulations 2002 (ESQCR). ESQCR 2002 apply only to Great Britain. There is a separate legislative framework in Northern Ireland, the Electricity Safety, Quality and Continuity Regulations (Northern Ireland) 2012, that are enforced by HSENI


    from (here - a parliamentary question)

    Does anyone have a list of differences