However, it seems to me that any given code should be accompanied by a clear indication of the reasons the call has been made along with a reference to at least the most pertinent regulation that has been breached.
lyledunn:
I have had a look through, albeit, ESQCR(NI), but cannot find anything specific that prohibits the connection of a consumer earth to Distributor neutral other than a consumer cannot combine the function of neutral and earth in a single conductor.
If anyone has a reference I would appreciate it.
But doesn't that arrangement make the Neutral a PEN conductor beyond the service head? And hence this consumer is combining the function of neutral and earth in a single conductor downstream of the point at which the distributor split the two?
lyledunn:
I take your point Graham but I read that more as a stipulation that a consumer cannot use a TNC type approach to the wiring within his installation. So in this particular case the function of neutral and earth beyond the service head will be in parallel conductors not in a single one.
I'm confused - what's the IE requirement? Is it to connect the supplier's N to a local electrode (MEN style), or is it to connect the installation's protective conductors to the installation's neutral conductors and then to the supplier's CNE? Or are you saying the supplier provided separate N and PE but the consumer has to connect them together again?
- Andy.