whjohnson:
So how would you code the lack of one for an EICR? Would you fail the installation?
Good question and I take the point! The argument for SPD (save in a hospital) is purely economic, so no code or C3. AFDD is intended to improve safety, but without it, we still have two faults required to danger so could not be more than C3.
If you want to be very strict, you could argue that the absence of recommended AFDD already requires improvement so C3! ?