Sparkingchip:
Hardwired smoke and heat alarms are a fire alarm system and their installation is within the scope of BS7671, you cannot just ignore them when you are doing an EICR.
If you are not inspecting and testing the wiring for an alarm system of any type for an EICR you have to specifically state on the EICR that they are excluded from the report and the client needs to get a report from a specialist company.
How an electrician or inspector could justify not inspecting and testing a mains voltage smoke alarm circuit for an EICR is beyond me, as is how they could inspect and test the smoke alarm circuit but not say that the actual alarms are not fit for purpose, because for example they expired several years ago.
The heffalump trap here is whether you I&T the alarm system - i.e. does it function as it should? If you are going to do that, you will need appropriate training and PI insurance.
I suggest that it is sufficient to unclip (a sample of) the smoke/heat alarms and inspect the cable and terminations. Then do IR (if you have not done a whole board check), Zs, and RCD (if fitted and not already tested) on the circuit as with any other circuit.
As for a panel system, I would stop short at inspecting and testing the supply.
Sparkingchip:
Hardwired smoke and heat alarms are a fire alarm system and their installation is within the scope of BS7671, you cannot just ignore them when you are doing an EICR.
If you are not inspecting and testing the wiring for an alarm system of any type for an EICR you have to specifically state on the EICR that they are excluded from the report and the client needs to get a report from a specialist company.
How an electrician or inspector could justify not inspecting and testing a mains voltage smoke alarm circuit for an EICR is beyond me, as is how they could inspect and test the smoke alarm circuit but not say that the actual alarms are not fit for purpose, because for example they expired several years ago.
The heffalump trap here is whether you I&T the alarm system - i.e. does it function as it should? If you are going to do that, you will need appropriate training and PI insurance.
I suggest that it is sufficient to unclip (a sample of) the smoke/heat alarms and inspect the cable and terminations. Then do IR (if you have not done a whole board check), Zs, and RCD (if fitted and not already tested) on the circuit as with any other circuit.
As for a panel system, I would stop short at inspecting and testing the supply.