The earth is so that the panel can flag a wire to earth fault if cabling insulation is mechanically damaged- a positive to earth fault or a negative to earth fault means the cable has been spiked, but the rest of the self test to see the terminator resistor may still pass.
As I see it the earth (C.P.C.) wire and "tin foil" are used with FP200 cable just because they are integral to the cable. The fire alarm panel will detect a fault if a nail is driven through a cable even if it is not earthed, in these cases.
1. Broken positive conductor.
2. Broken negative conductor.
3. Short between the two above.
Earth NOT needed in all three cases.
The cable only carries 24 Volts at a tiny current. And all components are made of plastic. Earth not needed.
Perhaps the screen protects the cables from strong magnetic fields or radio interference. I am not really sure on that.
Z.
The earth is so that the panel can flag a wire to earth fault if cabling insulation is mechanically damaged- a positive to earth fault or a negative to earth fault means the cable has been spiked, but the rest of the self test to see the terminator resistor may still pass.
As I see it the earth (C.P.C.) wire and "tin foil" are used with FP200 cable just because they are integral to the cable. The fire alarm panel will detect a fault if a nail is driven through a cable even if it is not earthed, in these cases.
1. Broken positive conductor.
2. Broken negative conductor.
3. Short between the two above.
Earth NOT needed in all three cases.
The cable only carries 24 Volts at a tiny current. And all components are made of plastic. Earth not needed.
Perhaps the screen protects the cables from strong magnetic fields or radio interference. I am not really sure on that.
Z.