I listened to Paul Meenan and and Tom Nagy discussing foundation earthing on the way home tonight and these Condudiscs were being recommended, but they dodged saying how much they cost, they did say that including one in a quote could make you uncompetitive.
So what sort of price are they?
For one disc and two bags of conducrete (which is what is recommended) it comes to £250.
the safer installation method and savings on labour installing them safely needs consideration. Comparing labour costs with drilling rods into the ground with no consideration of service strikes is comparing apples and pears.
If it's a consistent Zs reading of say 300 Ohms, it will easily satisfy the requirements of Table 41.5 up to 100mA operating current R.C.D.s, including the popular 30mA type. Of course I do not know if you radio people need a lower resistance to true earth for other reasons.
Earth electrode resistances above 200 Ω are considered unstable. This is also stated in the notes to Table 41.5.
Not very impressive 300 ohms is a bit high maybe if its buried deeper it will be better think ide stick to rods if given a choice
BS 7430 tell us that parts of earth electrodes buried at depths of less than 600 mm may not be effective due to frost and frost-heave. Terminations for buried electrodes (of all types) should be at least 250 mm below ground, in a suitable pit.
There are other alternatives, such as earthing mats (as small as 600 mm square).
In many locations, there are very good reasons why driven rod type electrodes, whilst cheap, may not be the best alternative - not least, risk of underground services strike, or rocky ground at the depths below soil surface we are considering.
I've to dig a couple of trenches for swa supplies to a garage and workshop. Would you suggest I lay a tape in there whilst I'm at it? Anything special about terminating the tape? (I've never seen it, let alone installed it!)
As JP says, depends on soil conditions. The electrodes need to be at least 600 mm deep because of frost (BS 7430) ... the SWA is recommended to be at least 500 mm (although Sections 705, 708, 740 etc. require at least 600 mm in general, with Section 705 further requires > 1000 mm in cultivated ground and I would recommend keeping to this for the electrodes also).