Can we interpolate what a likely 6A B, C, D might be suggested?
You could use the second method (4.2) if I(peak) and t(H50) are available from the driver manufacturers literature. Using their example;
For a 6 A ((In) MCB/RCBO and a load of 100 A LED driver peak inrush current (Ipeak) with a duration of 200 µs (tH50): using the chart above, Ipeak /In = 100/6 = 16.7 which correlates to 0.5 ms non-tripping time which is greater than the 200 µs peak inrush current time duration, therefore a Type B circuit breaker can be selected. If tH50 > 0.5 ms, a Type C or Type D MCB/RCBO would need to be selected.
I have read here ADLT - LED Driver Inrush Currents Technical Paper that "The line impedance has a significant effect on the peak and duration of the inrush current." so that summing the inrush currents may not be appropriate. Not sure why this would be, might be voltage drop, but using a C or D type, would not only allow higher levels of inrush through without tripping, but due to lower Zs required in circuits protected by them to achieve ADS, lower line impedance would also be present i assume.
Edit; I am also surprised that up to 3.5mA leakage current is allowed by BS EN 60598-1, per luminaire. Seems very high and would only allow a few luminaires to be fitted before RCD tripping occurred. I understand that there may be a few lamps per luminaire. But if your B-type RCBO started tripping, you changed it for a c type and it still tripped you might be scratching your head.